Sure....as long as it's not a FURNACE motor.:cool:

Of course not.

The argument that mainly comes up is that the attic fan is part of air conditioning equipment.


220.53 Appliance Load — Dwelling Unit(s). It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space- heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two- family, or multifamily dwelling.
 

MyCleveland

Senior Member
Location
Cleveland, Ohio
Of course not.

The argument that mainly comes up is that the attic fan is part of air conditioning equipment.


220.53 Appliance Load — Dwelling Unit(s). It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space- heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two- family, or multifamily dwelling.
Sorry Jumper...when I saw the post I immediately recalled your defense of furnace motors a few weeks back and was just trying for a funny.
Swing and miss.
 

kwired

Electron manager
Location
NE Nebraska
Of course not.

The argument that mainly comes up is that the attic fan is part of air conditioning equipment.


220.53 Appliance Load — Dwelling Unit(s). It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space- heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two- family, or multifamily dwelling.
IMO if it is not acting on the air of the occupied space it is not air conditioning equipment. Even then "Air conditioning equipment" to NEC typically contains a hermetic refrigerant compressor. See 440.1.

These are just ventilation appliances in nearly all instances.

By the nature of their intended operation I probably wouldn't apply a demand factor to them though. If you a large roof and four or more of them - they typically will run for more then three hours when they are called on to run.

Most are less then 300 VA or 1/8 hp. Should you forget to include them in the load calculation, they probably do not throw you off any significant amount.
 