Attic fan

Status
Not open for further replies.
Sure....as long as it's not a FURNACE motor.:cool:

Of course not.

The argument that mainly comes up is that the attic fan is part of air conditioning equipment.


220.53 Appliance Load — Dwelling Unit(s). It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space- heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two- family, or multifamily dwelling.
 
Of course not.

The argument that mainly comes up is that the attic fan is part of air conditioning equipment.


220.53 Appliance Load — Dwelling Unit(s). It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space- heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two- family, or multifamily dwelling.
Sorry Jumper...when I saw the post I immediately recalled your defense of furnace motors a few weeks back and was just trying for a funny.
Swing and miss.
 
Of course not.

The argument that mainly comes up is that the attic fan is part of air conditioning equipment.


220.53 Appliance Load — Dwelling Unit(s). It shall be permissible to apply a demand factor of 75 percent to the nameplate rating load of four or more appliances fastened in place, other than electric ranges, clothes dryers, space- heating equipment, or air-conditioning equipment, that are served by the same feeder or service in a one-family, two- family, or multifamily dwelling.
IMO if it is not acting on the air of the occupied space it is not air conditioning equipment. Even then "Air conditioning equipment" to NEC typically contains a hermetic refrigerant compressor. See 440.1.

These are just ventilation appliances in nearly all instances.

By the nature of their intended operation I probably wouldn't apply a demand factor to them though. If you a large roof and four or more of them - they typically will run for more then three hours when they are called on to run.

Most are less then 300 VA or 1/8 hp. Should you forget to include them in the load calculation, they probably do not throw you off any significant amount.
 