Yes, Inside stair-- it is clear in 210.70 as I have said many times.
First they do not meet the definition of stairways.
Second
(c) Where one or more lighting outlet(s)
are installed
for interior stairways, there shall be a wall switch at each
floor level, and landing level that includes an entryway, to
control the lighting outlet(s) where the stairway between
floor levels has six risers or more.
The attic does not count as a floor or story. So 210.70 does not apply.
It is 'implied' the this section does not apply to pull down stairs.
Also note that the light is for seeing once you are up there NOT for the stairs.
311.5.7 Illumination.
All stairs shall be provided with illumination in accordance with Section 303.6.
303.6 Stairway illumination.
All interior and exterior stairways shall be provided with a means to illuminate the stairs, including the landings and treads. Interior stairways shall be provided with an artificial light source located in the immediate vicinity of each landing of the stairway. For interior stairs the artificial light sources shall be capable of illuminating treads and landings to levels not less than 1 foot-candles (11 lux) measured at the center of treads and landings. Exterior stairways shall be provided with an artificial light source located in the immediate vicinity of the top landing of the stairway. Exterior stairways providing access to a basement from the outside grade level shall be provided with an artificial light source located in the immediate vicinity of the bottom landing of the stairway.