Have an open auditorium space client is looking for for budget/DB. Believe NEC lists lighting requirements for certain spaces, correct? Where would I find that? Thanks
NEc has general lighting loads for load calculating purposes in art 220, but has no requirements when it comes to illumination levels. Other then possibly some illumination levels for some specific application maybe located somewhere in chapters 5-6-7. There are places where NEC requires illumination, but doesn't generally say how much illumination.Have an open auditorium space client is looking for for budget/DB. Believe NEC lists lighting requirements for certain spaces, correct? Where would I find that? Thanks
Believe NEC lists lighting requirements for certain spaces, correct?
I'm doing a theater in NYC. The client wants dimming capabilities so we reached out to the fire marshal and they informed us that dimming is fine as long as the lights go to 100% illumination automatically when the fire alarm activates. This takes a relay to overide any dimming controls.