Looked at a new job today , complete rewiring of an auto repair shop,

Any tips things I should consider?

I know gfcis for receptacles for personal

I'm thinking led high bays roughly 16 foot ceilings.

Sent from my SM-G986U using Tapatalk
 
Looked at a new job today , complete rewiring of an auto repair shop,

Any tips things I should consider?

I know gfcis for receptacles for personal

I'm thinking led high bays roughly 16 foot ceilings.

Sent from my SM-G986U using Tapatalk
Last one I did I made it a point not to wrap the conduit all the way around the shop at 5’.
I ran the conduit at the ceiling line and dropped down for the outlets.
One reason for the rewire was to repair all the broken and bent conduit where practically everything was either hung from, tied off to, or something was slammed up against the conduit
 
Have you looked at Art 511 ?
There are some basic points (major vs minor repair) as well as other issues in that Article you need to review.
 
I was under the impression unless air flow certified by an engineer exempted the areas all repair garages had some areas such as within 18"of the floor were classified
 