The ATS in the oneline only has one source.
If that is represented correctly, then you should use a contactor with a voltage sensing relay to island the solar / battery source. Since this wouldn't be a NRTL listed system (the contactor / protective relay actuating the island mode), it would be interesting to see if an AHJ would bust your chops.
If that is represented correctly, then you should use a contactor with a voltage sensing relay to island the solar / battery source. Since this wouldn't be a NRTL listed system (the contactor / protective relay actuating the island mode), it would be interesting to see if an AHJ would bust your chops.