JimmyMac
- Louisville, KY, USA
1) NEC 2017 Art. 500.8(B)(1) states "...In addition, Class I equipment shall not have any exposed surface that operates at a temperature in excess of the autoignition temperature of the specific gas or vapor". Art. 500.8(D)(1) states "The temperature marking specified in TABLE 500.8(C) shall not exceed the autoignition temperature of the specific gas or vapor to be encountered". Art. 501.130(A) is related to Class I, Division 1 luminaire installations and does not mention anything about autoignition temperatures, surface temperatures, or T-codes. I would take this to mean that in Class I Div 1 areas, the luminaires' surface temperature must not exceed the autoignition temperature of the gas or vapor present and must contain a T-code whose temperature does not exceed the autoignition temperature (AIT) of the specific gas or vapor present (in addition to meeting CID1 area). True? If I have misinterpreted this , please help me to better understand.
2) NEC 2017 Art. 501.130(B)(1) is related to Class I, Division 2 installations and states "Where lamps are of a size or type that may, under normal operating conditions, reach surface temperatures exceeding 80 percent of the autoignition temperature (AIT) in degrees Celsius of the gas or vapor involved, luminaires shall comply with 501.130(A)(1) or shall be of a type that has been tested in order to determine the marked operating temperature or temperature class (T code)." It appears that maybe the requirements for a Class I Div 2 luminaire are more stringent than for a Class I Div.1 luminaire. Isn't the T-code a requirement anyway? Am I meeting code if I specify a luminaire for a Class I Div. 2 area that is rated Class I, Div. 2 and carries a T-code whose temperature is less than the autoignition temperature of the specific gas or vapor present? I want to make sure that i am not misinterpreting and that the T-Code must be equal to or less than 80% the AIT of the gas or vapor present.
Thanks for your help!