Is the "clearer explanation" the last sentance of 130.2(C)(1)?
Sort of, but that is a little misleading also. The first issue here is justification (130.1 (A)). If you pass that section then you need to look at note 1 in table 130.2(C) that refers you to the definition (Does not clear much up) and annex C, C.1.2.4. While the annexes are not part of the requirements they are for informational purposes to explain just this type of grey area. That section says to cross the PAB the qualified person
must do the following:
1. Have specified training to work on energized conductors or circuit parts (This is the key here, the company needs to have this special training documented, I have only seen utilities go this far, this training is over and above your basic safety training)
2. Have a documented plan justifying the need to work that close (EEWP)
3. Perform a risk analysis
4. Have the plan and the risk analysis approved by authorized management
5. Use PPE that is appropriate for working on exposed energized conductors or circuit parts...
Also look at C.1.2.3 (3) for RAB, "Be sure no part of the body enters the prohibited space"