autotransformer sanity check

Status
Not open for further replies.
A Please see attached image for data plate. The application is we have 120/208 supply and want 277/480 (neutral is needed for the 480 system). Do we use connect the supply neutral to the XO/HO terminal? I think yes just double checking. What would happen if one didnt?
 

Attachments

  • auto.jpg
    auto.jpg
    146.6 KB · Views: 9

mbrooke

Batteries Included
Location
United States
Occupation
Technician
For step-up:
You do NOT connect the X0 terminal on the 208V side.
You DO connect the X0 on the 480V side.



Then how do you deal with zero sequence currents? Or preventing distortion of the L-N voltage vector?


The neutral of the 208 and 480 volt systems need to be tied solidly together while the EGCs do not connect to the X0/H0- just the chassis. This is not a separately derived system. The 480 is just a continuum of the 208.
 

mike_kilroy

Senior Member
Location
United States
Then how do you deal with zero sequence currents? Or preventing distortion of the L-N voltage vector?


The neutral of the 208 and 480 volt systems need to be tied solidly together while the EGCs do not connect to the X0/H0- just the chassis. This is not a separately derived system. The 480 is just a continuum of the 208.
Agree, tie both together. I think jraef is thinking of the more common back feeding a wye (secondary) isolation xfmr as primary.

Sent from my SM-G900V using Tapatalk
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Agree, tie both together. I think jraef is thinking of the more common back feeding a wye (secondary) isolation xfmr as primary.

Sent from my SM-G900V using Tapatalk

I wold say so- a wye delta. In that case DO NOT ground the primary. Very bad things will come of it.
 
Agree, tie both together. I think jraef is thinking of the more common back feeding a wye (secondary) isolation xfmr as primary.

Sent from my SM-G900V using Tapatalk

Ok, yeah I am aware of that one and perhaps that is why I am paranoid about connecting the 208 neutral. I was expecting to receive an isolation transformer for this job so the auto threw me for a loop.
 

mike_kilroy

Senior Member
Location
United States
The transformer would make a neutral so it seems plausible that you wouldn't need to supply one, that was my thinking.
And I agree with you too. It would have made you a good 480 neutral, but seems more robust tying. Great question.

Some (most?) 208Y DO tie X0 to EGC so not sure why to keep it separate? Doesn't every 120v circuit get the X0 tied to EGC in each breaker panel? Maybe worth more discussion on that?

Sent from my SM-G900V using Tapatalk
 

Besoeker

Senior Member
Location
UK
For step-up:
You do NOT connect the X0 terminal on the 208V side.
You DO connect the X0 on the 480V side.
It's an autotransformer.
The 208V and the 480V are taps on the same winding. "Sides" don't really come into it.
What am I missing?
 

kwired

Electron manager
Location
NE Nebraska
The transformer would make a neutral so it seems plausible that you wouldn't need to supply one, that was my thinking.
but if you have an unbalance as a result of 120 volt load on one phase - the neutral voltage may shift as a result of load balancing - having primary neutral tied to center of the wye will stabilize neutral voltage regardless of current imbalance - within a reasonable range anyway.

Separate windings like a isolation transformer has is different.
 

mike_kilroy

Senior Member
Location
United States
Right but you will have an incoming and outgoing neutral, seems they would give you two terminals or a double lug

We use DIN rail mounted dead front terminals on our transformers. Perhaps they did too? If so, YOU could buy one and slip it in on the DIN rail to make your connections nicer? On the same note, aren't TWO wires allowed per terminal per NEC/NFPA, etc? Remember the X0 is generally not a current carrying point (unless an old SCR drive system, etc.) so might be able to be smaller gauge? I am not sure on this point for your case - just bringing it up as idea in case you do not add a second terminal.
 