And my wit was wasted............It has been established that jraef missed that it was an auto not an isolation. That has been settled.
And my wit was wasted............It has been established that jraef missed that it was an auto not an isolation. That has been settled.
And my wit was wasted............
And I agree with you too. It would have made you a good 480 neutral, but seems more robust tying. Great question.
A wye autotransformer does not do a good job of deriving a neutral. If you only connected X1, X2, and X3 then H0 would vary quite a bit due to any imbalance on H1, H2, H3.
It could be made to work by using an unconnected 'secondary' set of delta windings. These would not have any external connection, but circulating currents on the delta would act to stabilize H0.
It could also be made to work if you had some sort of 'zig-zag' winding, where each leg of the core has two phases on it. Difficult to do with all those different voltage connections, but possible.
All in all the easiest thing to do is simply connect X0 to the supply neutral.
-Jon
I don't see how you can separate the X0 & H0 on an auto since they share the same wire. Its not like the H wdg and X wdg are on two separate bobbins around the core. Seems like the only way to stabilize the neutral is to tie it (X0/H0) to a solid ground. I thought a zig-zag provided a medium to high impedance ground.
I don't see how you can separate the X0 & H0 on an auto since they share the same wire. Its not like the H wdg and X wdg are on two separate bobbins around the core. Seems like the only way to stabilize the neutral is to tie it (X0/H0) to a solid ground. I thought a zig-zag provided a medium to high impedance ground.
I don't see how you can separate the X0 & H0 on an auto since they share the same wire. Its not like the H wdg and X wdg are on two separate bobbins around the core. Seems like the only way to stabilize the neutral is to tie it (X0/H0) to a solid ground. I thought a zig-zag provided a medium to high impedance ground.
If you were supplying only balanced three phase loads and no line to neutral loads, I don't see that you need to tie anything to the wye point.I don't see how you can separate the X0 & H0 on an auto since they share the same wire. Its not like the H wdg and X wdg are on two separate bobbins around the core. Seems like the only way to stabilize the neutral is to tie it (X0/H0) to a solid ground. I thought a zig-zag provided a medium to high impedance ground.
"Neutral" in this case is a common point to both the high and low voltage leads, there is no true input and output neutral like there could be on a separately derived system. Same concept as the common lead on a single phase autotransformer - it is simply one point in that system - it is very likely also the grounded conductor of the supply circuit, but there isn't really a secondary circuit, just taps on a coil(s) that give you different voltages based on how many turns there are between each point being measured.]
Bugman, for discussion clarity, no one suggested separating Xo and Ho IN THE TRANSFORMER.
The discussion was whether OP should bring his present Xo into this xfmr's Xo/Ho or not (and thus tie HIS neutral to output neutral or not)...
]
Bugman, for discussion clarity, no one suggested separating Xo and Ho IN THE TRANSFORMER.
The discussion was whether OP should bring his present Xo into this xfmr's Xo/Ho or not (and thus tie HIS neutral to output neutral or not)...
If you were supplying only balanced three phase loads and no line to neutral loads, I don't see that you need to tie anything to the wye point.
In my case, although I didnt state it, The "load" is a three phase PV inverter. I am 98% sure that the neutral is just used for phase monitoring and carries little to no current and that the output is very closely balanced. Thus perhaps we didntt need to bring the supply neutral from the 208 source for this application.
Right. The transformer would - in true autotransformer fashion - derive the neutral with the three X phases, then you could use it for the H/load. That was the thinking.
In my case, although I didnt state it, The "load" is a three phase PV inverter. I am 98% sure that the neutral is just used for phase monitoring and carries little to no current and that the output is very closely balanced. Thus perhaps we didntt need to bring the supply neutral from the 208 source for this application.
Unfortunately this is not correct for a wye-wye 3 phase autotransformer. It would work for a single phase autotransfomer, and it would work for a zig-zag transformer, but in a wye-wye autotransformer the neutral simply is not stable. If you lightly load one phase then reduced current would flow on that leg, and the leg to X0/H0 voltage would climb, in the limit to almost the line-neutral voltage.
In this case, with a well balanced load and little neutral current, the system might work, but I would not trust it.
-Jon
Unfortunately this is not correct for a wye-wye 3 phase autotransformer. It would work for a single phase autotransfomer, and it would work for a zig-zag transformer, but in a wye-wye autotransformer the neutral simply is not stable. If you lightly load one phase then reduced current would flow on that leg, and the leg to X0/H0 voltage would climb, in the limit to almost the line-neutral voltage.
In this case, with a well balanced load and little neutral current, the system might work, but I would not trust it.
-Jon
It seems to me that if you have a wye-wye *autotransformer* the H0 and X0 are exactly the same point!
How can that be unstable?...
It seems to me that if you have a wye-wye *autotransformer* the H0 and X0 are exactly the same point!
How can that be unstable?
Sent from my XT1585 using Tapatalk
That's what I thought from the very beginning, and I'm still hoping to learn something, but it makes me feel good to think we are coming back to that.
.
They are not the same point if not bonded together. Your conditions 2 and 3 each leave one point or the other "floating". When things are balanced they will be at/very near same potential. Throw some unbalance in there and one or the other will drift potential wise from the other. Bond them together and you force them to be same potential regardless of balance condition.Yes they are the same point, no question about that. The discussion is about running a neutral with the supply, or not and letting the transformer derive the neutral for the load. We have three possibilities (#3 is new, I dont think it has been discussed yet):
1. supply neutral and load neutral both get landed to the common XO/HO terminal
2. Only the load neutral gets landed on the XO/HO terminal and no neutral is run with the supply.
3. Run the supply neutral to the load without hitting the XO/HO terminal.
What would happen for #3?