Autotransformer up-rating

Status
Not open for further replies.

hirsch56

Member
I need a 120/240V -> 12/24V Xformer to serve as a boost autotransformer giving 230V, 20A output. My question is: Can I get by with the .75kVA Xformer in hand? In a normal primary/secondary application one would need ~5kVA, but when wired as an autotransformer, don't kVAs get up-rated by a factor of 10? Is that correct?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
hirsch56 said:
I need a 120/240V -> 12/24V Xformer to serve as a boost autotransformer giving 230V, 20A output. My question is: Can I get by with the .75kVA Xformer in hand? In a normal primary/secondary application one would need ~5kVA, but when wired as an autotransformer, don't kVAs get up-rated by a factor of 10? Is that correct?

Actually you only need a 250VA unit.
The final ratio of the autotransformer determines the "factor".

I use the on-line buck-boost calculator from Square D.
http://www.squared.com/us/squared/corporate_info.nsf/unid/C16C1C0106A0374985256A5400653380/$file/softwareFrameset.htm
 

hirsch56

Member
I tried the Square-D on-line calculator, but it gives me a 4.7kVA answer. How do you come up with 250VA? Input will be 208V and output 230V.
 

hirsch56

Member
OK, I see that the calculator is saying there's a 4.7kVA load, but the Xformer it is recommending is a 0.5kVA model. That's what I thought, that it can be uprated by a factor of 10. You're saying that the factor of 10 comes from the fact that it is a divide by 10 Xformer (240 -> 24). Likewise, if the Xformer was 240 -> 36V, that's a factor of 6.7, so a 4.7kVA load could run from a 0.705 kVA unit. I get it!! Thank you Jim!
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I think the math comes from the difference in voltage times the current.

Since you are stepping up 10 volts, its 10V * 20A = 200VA. If you were going from 208V to 240V, it would be 32V* 20A = 640VA. (At least this works for one configuration of a autotransformer, since the current cancels out in the part of the coil with the common voltages.)

Why do you need to change from 240V to 230V?? Motors and equipment with a 230V rating on them are normally connected to a 240V supply.

Steve
 

hirsch56

Member
OK, Steve. You're saying to multiply the step voltage by the output current. That makes more sense.

I am changing 208V, 1ph. to 230V/20A to run a helium cold-head. In the ideal case, I can turn 208 into 229 with a 240/24V Xformer. A 21V step times 20A needs 420VA. The Xformer I have on hand is a 240/32V, 750VA. Instead of 229V it will give me 236V. I'll ask the OEM if 236V is close enough, so I might avoid buying a different Xformer.

Thanks to all. This forum is very helpful. -Hirsch
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I'd say the 236v is ideal, since 230v motors are actually designed to run on 240v systems.
 