Situation is that I have a 208Y/120 service, and the pool pumps are 230v only. I have verified with Pentair that these IntellifloXF pumps will not work on 208v. The pool contractor needs these specific pumps for this install.
I can't find any mention of autotransformers in article 680. My plan at this point is to install the transformer at each pump location. We have 1" conduits that run from the pool panel under the equipment pad and up into a junction box center of the pad, and from there will branch out to the equipment.
Anyone see a reason this wouldn't be acceptable? In the past the contractor used 208v pumps when necessary but again, this specific 230v model is required.
Pic of area attached for reference ..... the junction box will be just in front of that large gas heater. Conduit will extend from there to each of the 3 pumps. I would set a strut mount next to the pump to mount the buck/boost.
Sent from my iPhone using Tapatalk
I can't find any mention of autotransformers in article 680. My plan at this point is to install the transformer at each pump location. We have 1" conduits that run from the pool panel under the equipment pad and up into a junction box center of the pad, and from there will branch out to the equipment.
Anyone see a reason this wouldn't be acceptable? In the past the contractor used 208v pumps when necessary but again, this specific 230v model is required.
Pic of area attached for reference ..... the junction box will be just in front of that large gas heater. Conduit will extend from there to each of the 3 pumps. I would set a strut mount next to the pump to mount the buck/boost.