Because the supply is 20A 240v single phase, I believe the GFCI rule still applies.
I agree, it is a single phase branch circuit, what happens to it in the pump is not relevant.
Because the supply is 20A 240v single phase, I believe the GFCI rule still applies.
My bad, I think. I kept thinking of the "Pentair" cabinet pictured in your OP and was thinking it was the VFD and the motor was remote from it.The supply is 240v single phase..... there is a DC inverter inside the pump, and then it converts to 3-phase AC to power the VFD.
The pump in question is a Pentair IntellifloXF. http://www.pentairpool.com/products/pumps-inground-intellifloxf-variable-speed-pump-452.htm
Because the supply is 20A 240v single phase, I believe the GFCI rule still applies.