- Occupation
- Electrical Engineer
I got a 700ft run for a 100A 240 load to a marine dock. At full load of 80% (or 80 amps) voltage drop is 22 volts. I want to use an autotransformer to boost the voltage. I would use a 240/120 - 32/16V autotransformer. Primary windings would be in series wired at 240V, the secondary side would have the 16V winding in each of the two phase conductors. The neutral conductor would just carry through on both sides of the transformer. I know how to size the transformer kva, but my question is on the secondary. The secondary coils have polarity to the primary, usually shown as dots on a diagram. But the transformers I'm seeing don't show this polarity. So, how can I know in advance how to wire the secondary conductors so they both boost. I know I could just turn it on and measure the voltage and reverse the leads if necessary, but how do I know in advance. What is the correct orientation of the X terminals to have both legs boost voltage.