jrexrode said:
			The wiring diagram shows the winding with a center tap coming off of it.
    1                       3
    1           |           3
                 2
Primary volts 240. Connect Primary lines to 1-3.
Secondary volts.                      Connect secondary lines
240                                         1-3
120                                         1-2 or 2-3
120/240                                  1-2-3
jrex -
I just figured out my last post wasn't particularly useful.
Here's what I think you have:
Assume High leg delta, A-N=120, C-N=120, B-N=208.  The neutral is likely bonded to earth (ground, building steel)
You have the two phases (240V) out at the machine, but no neutral.  But, you need a 120V control circuit, and you likely want it grounded to maintain code compliance.  So, when you connect the autotransformer, you get 120V from the centertap to each end.  All this is pretty much as you said, just restated to make sure I understood.
Now, I think you are asking, "How do I earth this auto transformer to get a 120V control circuit that is bonded (or maybe "referenced" is a better word) to earth?"
Following jon's post, depending on which two phases are out at the machine, the answer is either, "You can't"; or "You shouldn't".
If you have A-B or C-B out there, then from your typed sketch,
Term 1 (A or C) to ground = 120V
Term 3 (B) to ground = 208V
Term 2 (center tap) to ground = 120V
Yep, that's truth.  Draw a vector diagram and it will be clear.
Now, if you have A-C , then
A - G = 120V
C - G = 120V
Center tap - G = NEAR ZERO (which is not exactly zero)
Even a few tenths of a volt could give some hellacious circulating currents.
So, following this reasoning, the answer is, "pitch the auto transformer and get a two winding xfm."
Hope this post helps (or, I'm all wet and still no help)
carl