TL;DR: Do most commercial/industrial electrical services use the exemption in NEC 110.24(B), or is this rule just rarely enforced?
Hi everyone,
I’ve had several inspectors ask for available fault current labeling on our PV installations, for both load-side and line-side points of interconnection. From what I understand, only two NEC rules directly address fault current labeling: 110.16(B) and 110.24(B).
So my questions are:
Most of our work is under the 2017 NEC.
Thanks in advance for your insights!
Hi everyone,
I’ve had several inspectors ask for available fault current labeling on our PV installations, for both load-side and line-side points of interconnection. From what I understand, only two NEC rules directly address fault current labeling: 110.16(B) and 110.24(B).
- Load-side systems:
Our installations don’t involve service equipment, so 110.16(B) doesn’t apply. - Line-side systems:
Our AC disconnect is considered service equipment. If rated at 1200A or more, the labeling in 110.16(B) applies.
So my questions are:
- Is this rule often unenforced, or are these facilities relying on the 110.24(B) exception (industrial facilities exempt when only qualified persons service the equipment)?
- If the exception is commonly used, can I argue that it should apply to our PV installations?
- If this is a case of inconsistent enforcement, how do I handle being asked to update a nonexistent label on equipment we didn’t install?
Most of our work is under the 2017 NEC.
Thanks in advance for your insights!