I am working with a consulting engineer to provide the 110.16(B) labeling on a project. As a part of their analysis, they shared a different take on the SCCR or "withstand rating" of inverters. The consulting engineer interprets the "AC Surge Protection" spec as a withstand rating that specifies a maximum available fault current (AFC). In the case of the CPS 60kW string inverter, this value is 15kA. Here is a link to the spec sheet.
I'm curious to hear from the folks on this forum if this is a valid interpretation, given that other posts on this thread seem to be of the opinion that inverters do not have a max AFC spec. In my specific case, I am being asked to install a current-limited, fused, AC disconnect upstream of my AC inverter combiner panel in order to keep the AFC below the AC surge protection rating of 15kA.
Assuming this is a valid interpretation and important spec to design around, has anyone used any other method (aside from a fused disco) to achieve the same level of protection?
I'm curious to hear from the folks on this forum if this is a valid interpretation, given that other posts on this thread seem to be of the opinion that inverters do not have a max AFC spec. In my specific case, I am being asked to install a current-limited, fused, AC disconnect upstream of my AC inverter combiner panel in order to keep the AFC below the AC surge protection rating of 15kA.
Assuming this is a valid interpretation and important spec to design around, has anyone used any other method (aside from a fused disco) to achieve the same level of protection?