kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
The panels in question were almost all control panels. I believe the NEC requires the SCCR of an industrial control panel to meet or exceed the available fault current of the feeder or branch supplying it. Don't have the code handy to look up the articles but there are lots of papers and what not out there from the circuit protection manufacturers about compliance. Some sources I look at say this DOES affect arc flash calculations but I am not expert on arc flash at all.
If the SCCR of any component is exceeded by the ability of the supply, there is risk of a violent failure when a failure happens. NEC is in general not going to support exceeding ratings and any exceptions would be pretty rare. I would like to think in absence of any other requirements ratings are marked on a device it would at least be a requirement of 110.3(B).
I am no expert at details of arc flash calculations either, but more available fault current means there is more available energy to release in an arc flash event. Some kind of hang themselves thinking higher voltage means more energy, but voltage alone means nothing, it is the combination of voltage, current and circuit impedance that determines power and energy at the incident location.