This is a class 2 power limited nurse call system. I have an existing 3 gang back box for a station where I intend on mounting a 1 gang station on each side. Typically I would just cut a ring in. This is a non fire rated wall. I'm hearing that I must put a box in with some flex to the 3 gang. Can you direct me to the code that dictates this. This is in a California hospital under the OSHPD jurisdiction enforcing the California Electrical Code. Thank You.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
See 517.80 and 517.81 in the NEC. If it is a local or Ca code requirement I can't help. :(