ItsHot said:
Hey Celtic, Do you believe so many of us are terrified about bac -stabs because a lot of us remember the days of aluminum branch circuit conductors. And the problems then. And the problem was with the aluminum wire being weak, not the method of back stabbing?
Of all of the stabbed-receptacle trouble-shooting calls I've done, and there have been many, only one was with aluminum conductors. Aluminum has its problems aplenty without the help of having been stabbed.
Many moons ago, I went on a T/S call for a dead bedroom addition. Someone fed the entire new bedroom from an existing receptacle, at the end of the line, fed with #12 aluminum. The original receptacle was blackened, as was the wall above it.
When we opened the wall above the scorched receptacle, the aluminum conductors were completely bare for about two feet above the receptacle box. They were shiny and bright, and there was absolutely no sign of insulation or sheath, as if it had evaporated.
The incredible thing was that the three conductors were perfectly paralleled as if the cable was still intact, but invisible, and that there was no sign of arcing or fire. It mad one thing clear: wire temperature limitation is based on the insulation, not the conductor.
360Youth said:
I pretty much check every device I stab with a little pull or an aquired feel . . .
I seem to remember a post not too long ago of a toasted outlet and wall that had its wires hooked, not stabbed. Neither method is a guarntee. IMO.
True enough, but the problem with stabbed terminations appears after years of adequate conductivity, first with intermittent contact, and then finally no power. Heat causes the spring metal to lose its springiness, which causes more heat, and it snowballs. But, it takes time, sometimes over 20 years.
Just last week, we had a service call for a master bedroom and bathroom half of the upstairs, and found it in the hall receptacle. Pulled out the receptacle and one conductor stayed in position as if the receptacle was still there. Happens every time.
tonyou812 said:
I know alot of electritians that say they never back stab but I have seen their work at times and they did it.
I don't, and I'll jump all over any of my guys who do it. Now, give me back-wired clamping terminals, like most GFCI receptacles have, and I'll use those all day long. Plus, many of them accept two conductors per screw, great for split-wired circuits.
celtic said:
Icky: Aye
Fast: Aye
Approved: Aye
The Ayes have it.