cschmid said:okay done with meetings...lets see you can use a 15 amp outlet on a 20 amp circuit which would have a 20 amp breaker..so at 16 amps you are now over the maximum rating of the outlet (which is back stabbed)by 6-1/2% now if you go to 18 amps you are almost 20% over the rating of the outlet and yet you have not reached the trip point of the circuit breaker..But the spring loaded holding mechanism is now 20% over its rating and now starts deterioration..Now you can see why it does not use the OCPD..
The flaw in your logic is the 20A ckt.
Back stabs do not fit on #12's...only #14's
Play again?