Back-up Portable Generator grounding requirements for residential applications

Status
Not open for further replies.

JELECT.

New User
Location
New York State
Occupation
Elactrician
What are the grounding, bonding, and grounding electrode NEC requirements, regarding the use of a portable generator used for back-up power to a residential home? this generator would be plugged into a 30 amp 125/250 volt 4 wire male inlet which connects to the main panelboard through a manually operated 30 amp, 2-pole circuit breaker that can only be closed by opening the main 100 amp service breaker which is mechanically interlocked with 30 amp breaker?
 
Last edited:

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Actually a 3 pole transfer switch for most residences since they are single phase. The requirement is to switch the ungrounded and neutral conductors on a bonded generator, and use a 3 wire feed. It may need a GEC too. For an unbonded generator, you don't switch the neutral and use a 4 wire feed.
 

tom baker

First Chief Moderator
Staff member
Please review section 702.7
The generator type, unbonded or bonded neutral, is matched to the type of transfer switch. Most generators are bonded neutral type. On a generator with gfci for its outlets, when used with a transfer switch that does not transfer the neutral, the gfci will trip.
 