The panel neutral bus will have to be driven through the GFCI breaker. HOW would this be done ?
Specifically, in line with the reversal of line and load roles, the feeder neutral wire will terminate at the neutral screw of the breaker and the neutral pigtail from the breaker will be the exclusive feed to the neutral bus.
If you get it backwards, any amount of neutral current at all will trip the GFCI.