Backfeed a 480Y to 240delta transformer... Awkward scenario.

Status
Not open for further replies.

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
That is a weird transformer.

Normally you have a delta primary and wye secondary, and then people try to figure out grounding when the transformer is reversed.

But this beastie is normally a wye primary delta secondary.

I'd suggest actually looking inside the enclosure...there might actually be an 'H0' terminal in there. If it exists, I'd contact the manufacturer again, and ask if you can use the H0 terminal for grounding when the transformer is backfed.

Also, this is a 'high efficiency' transformer. I'd be concerned about very high inrush current tripping the supply breaker on startup; you expect increased inrush current when you backfeed a transformer (relative to a similar technology transformer designed from the start with your required primary voltage); this might be worse with a 'high efficiency' transformer. (Or maybe not...I'm extrapolating from 'high efficiency' motors.)

-Jon
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
We like new guys just fine here.

I am still a bit leery on this idea of corner grounding a wye output/secondary though, but lotsa stuff I do not know.
If the output were 208Y/120 the provision about mandatory grounding of the neutral if it allowed less than 150V from each hot to ground would probably apply, even if the neutral was not used. But for 480 there does not seem to be a code restrictions against corner (end) grounding.
If the neutral were used, then the phase and system identification would be far from standard.

Sent from my XT1585 using Tapatalk
 

jumper

Senior Member
If the output were 208Y/120 the provision about mandatory grounding of the neutral if it allowed less than 150V from each hot to ground would probably apply, even if the neutral was not used. But for 480 there does not seem to be a code restrictions against corner (end) grounding.
If the neutral were used, then the phase and system identification would be far from standard.

Sent from my XT1585 using Tapatalk

Okay, still weird for me.
 
I have heard this can be an issue with these high efficiency transformers. That is the reason that manufacturers prefer not backfeeding transformers.




That is a weird transformer.

Normally you have a delta primary and wye secondary, and then people try to figure out grounding when the transformer is reversed.

But this beastie is normally a wye primary delta secondary.

I'd suggest actually looking inside the enclosure...there might actually be an 'H0' terminal in there. If it exists, I'd contact the manufacturer again, and ask if you can use the H0 terminal for grounding when the transformer is backfed.

Also, this is a 'high efficiency' transformer. I'd be concerned about very high inrush current tripping the supply breaker on startup; you expect increased inrush current when you backfeed a transformer (relative to a similar technology transformer designed from the start with your required primary voltage); this might be worse with a 'high efficiency' transformer. (Or maybe not...I'm extrapolating from 'high efficiency' motors.)

-Jon
 