ohmti787
- Orlando, FL
- Electrical Engineer
Looking at your diagram, I'm assuming (!) the sub-panel is to handle circuits to remain live in the event of a power failure.Hello,
In these scenarios, do I still need to install a main breaker in the subpanel to protect the feed through conductors?
Thanks!
I didn't see anything in his electrical drawing that indicates that there is a battery inverter in the system. Am I missing something?Looking at your diagram, I'm assuming (!) the sub-panel is to handle circuits to remain live in the event of a power failure.
Won't you need an interlocked main breaker in the sub panel to prevent back-feeding the mains?
no sir, that's the existing subpanel inside the home, being fed from the meter main outside. instead of installing our backfeed breaker in the meter main outside, and having to install a main breaker to protect the subpanel downstream, we decided to put the PV breaker in the subpanel instead so we don't need to buy that main breaker. but i'm having second thoughts about the potential of overloading the feed through conductors.Looking at your diagram, I'm assuming (!) the sub-panel is to handle circuits to remain live in the event of a power failure.
it's just solar. one string of panels with micros.I didn't see anything in his electrical drawing that indicates that there is a battery inverter in the system. Am I missing something?
How would that happen? Unless all the loads in the sub are all turned off, when it is running the PV will reduce the current in the feedthrough conductors, and if they are turned off, the PV can only push at most 20A back through the 150A conductors to the main panel. 705.12(B) is satisfied in both panels; I don't see the problem.no sir, that's the existing subpanel inside the home, being fed from the meter main outside. instead of installing our backfeed breaker in the meter main outside, and having to install a main breaker to protect the subpanel downstream, we decided to put the PV breaker in the subpanel instead so we don't need to buy that main breaker. but i'm having second thoughts about the potential of overloading the feed through conductors.
Perhaps abstractly, but not in the sense that matters here. Treating the assembly as a single composite panel is not supported by the code language, or by the reasons for it.With the connection to the subpanel having no OCPD, the cables are essentially bus bars.