Backstabs - fact or urban legend?
WMitch
Guys - I'm not looking to pick a fight here but comments about "backstab" receptacle connections piqued my interest. I'm a packrat when it comes to tools and hardware and I managed to dig up 18 used 15Amp receptacles in conditions ranging from like new to pretty ragged looking. I also have way too much time on my hands.
Anyway I decided to test the backstabs. All of them are the old style spring type. I put a 14 ga wire (stripped correctly) into one backstab hole on each receptacle and tried to pull it out. I could not get any to fail. I'm no Charles Atlas, but I ain't a wimp either. I know I was pulling at least 30-40 lbs.
While I understand that spring tension may decrease over time. I have 3 outlets in my shed that I wired to the backstabs. That was 20 years ago and tomorrow I'm gonna' take them out and test them the same way. I doubt if there will be any failures.
My questions are - If these things fail so much why doesn't the NEC disallow their use? Why does UL continue to list them if the design is inherently unsafe? More importantly, how many of you have really found a correctly assembled backstab that failed vs just passing on what they were taught/told?
Re: Backstabs - fact or urban legend?
How about we look at it the from the other direction?
Do you think it is remotely possible that the little contact area provide when using back stabs can provide as low a resistance connection as a screw terminal?
UL is not a quality assurance lab, all UL does is make sure that when a product is used properly that it is relatively safe.
Just because you can't physically pull out the wire doesn't prove electrical integrity. They usually cause intermittent problems. I've personally seen a number of these fail in my lifetime, albeit, they have been the older ones. I haven't seen any problems with new installations.
I don't believe they fail so much, at least not nearly as many that fail due to the improper use of the connection type. Most that I have seen over the years that failed or started causing problems were due to either the conductor not pushed in far enough or not enough insulation removed from the conductor.
They did take a step in the direction a few years ago when UL said that the back stab connection must be sized to accept only #14 wire, thereby limiting their use to 15 amp circuits.
Don
It has been my experiance on the old style outlets that allowed both #14 and #12 stabs that when you remove a conductor from the stab the correct way and then try to reinstall the conductor, that is when I have seen the wire pop right out. Scott
What's the feeling on the newer backwired components. I just installed a half dozen GFIs that had a screw driven clamp arrangement. Stick a properly sized (12 ga) and stripped wire in the hole and tighten the screw.
[ February 14, 2006, 05:30 PM: Message edited by: WMitch ]
That's a little different technology. I feel more comfortable with those.
Just pulled out a switch yesterday that controlled a few basement lights. It was backstabbed and when I pulled out the wires one connection was slightly melted and blackened. This was in use for about seven years. Not a good connection in my view.
Don
Interesting....do you have reference to cite?
(I'm no fan of back-stabbing, but need verification of your claim)
To many times to count, I have gone on a service call (both residential & commercial) and the complaint was something like: "We checked the breakers, but all these plugs quit working" Nine times out of ten, it will be a backstabed outlet. Half the time, it's the neutral.
By the way, what's everyone's opinion of these?
I bought a bunch of Halo light cans that had a smaller version. I tug tested the first one and it came off the fixture wire. I cut them off and used wire nuts.
[ February 14, 2006, 07:35 PM: Message edited by: WMitch ]
I agree with minuteman, I have pulled out many receptacles that were backstabbed and the neutral usually pops right out and shows definite arcing.
Yeah, if they was as big as that one... I would be scared!
[ February 14, 2006, 07:52 PM: Message edited by: Minuteman ]
My opinion is: I don't want to have to buy the junction boxes!
Well, okay the pic is huge, but I wonder how the long term connection will hold up. Will they also fail after long term, due to the small contact area?
[ February 14, 2006, 09:04 PM: Message edited by: Minuteman ]
A fair test would include years of daily, high-current pass-through use. Heat, not time, is what causes spring contact pressure to weaken.
The heat causes looseness, which causes more heat, and it slowly snowballs over time, similarly to current cycling in aluminum conductors.
WHY IS IT THAT AS I SCROLL DOWN I KEEP SEEING THIS BIG CHUNCK OF CHEESE :p
Have not used them for long enough yet to tell
they are faster
as far as backstab 9 out of 10 times the switch or receptical that is not working is due to a backstab or not twisting wires before putting on wire nuts at least that is what I find on the service calls I go on
those yellow things, or Wagos, are handy for those times where the wires are cut "handyman style", you know, they're so short you can't even get a wirenut to start on them. I have used them to latch on to the bare grounding wire when the previous (ahem) "installer" cut the useless thing off at the sheath. They make a pink one with 2 ports. I think those big yellow ones are for 750MCM aren't they?