I wasn't sure.Jim, do you think that I said something different?
It has little to do with instructions. It has a lot to do with the actual marking on the device. The NEC and UL standards require the words LINE and/or LOAD.
GE might make a breaker without the specific markings, Trane may mount this breaker in a roof top unit with the instructions to come in the bottom. Eaton might make a breaker marked with Line on top, Trane would not be allowed to bottom feed that breaker regardless what their instructions said.