I just replaced a 400a breaker. It was in a VFD sized for a 125 hp moter 480v 3p. 200a fuses and 3/0 copper thhn fed this VFD.Line side connections are ok. Load side phase 1 ok, phase 2 got very hot the insulation was brittel falling off and copper wire had color distortion for about 12in. phase 3 almost as bad as phase 2. The connections seemed tight, this vfd is only 18 months old. After repair amp draw was equal less than 90a each leg. What could cause this? john