Had a call from a new customer.
"I'm getting "shocked" when I touch my A/C compressor":-?
I turn off the breaker to the unit and open the disconnect....all is well.
Turn the breaker back on and check voltage.
238V line to line, 119V line A to ground, 238V line B to ground!
What the HEY?....The ground is energized (so was the disconnect enclosure, and the A/C unit enclosure).
Good thing I was working this like it was energized (which it was).
This was on a double wide mobile home, so I start at the beginning.
Open 200A disconnect at outside pole, looks OK.
4 wire 3/0cu feeder underground to house panel....all connections tight....overhead service looks OK.
Open breaker panel inside home, and both grounded feeder conductors are landed on the (isolated) Neutral bar:-?!!.....bonding strap removed.....Equipment grounds landed on terminal strip mounted to the metal enclosure....No grounding continuity!!
The equipment grounds were not bonded to the service ground!
Actually, they weren't bonded to anything other than every grounding conductor in the home.
I start checking receptacles in the home, and some have 238V between the grounding terminal and a phase leg (Line B).
What I've got is a floating ground circuit with a short(?) somewhere that's powering up the grounding circuit.
I leave my meter on one of the receptacles with the "hot" ground and start turning off breakers.
When I get to the range breaker and turn it off, the voltage on the ground goes away.
Un-plug the range, turn on the circuit and check again, voltage gone.
I pull the range out of it's space and check for continuity at the range cord.
Sure enough, one power leg shows continuity to ground....range is shorted.
I inform homeowner that the range is defective....he needs to call repair man.
I tell him to look for shorted wire...element...etc.
To correct the house grounding, I installed a lug on the breaker panel enclosure and moved one of the grounded feeders to this lug....making continuity between the panel enclosure, circuit grounding conductors and the service ground.
When I think of this situation...and I have a lot in the last couple of days...I realize that I may have saved someones life.
It's still sinking in how dangerous this situation was for the homeowners.
I asked the homeowner who installed the electrical service to his home, and he said that he and his son did.....16 years ago:roll:.
They had tried to troubleshoot this problem but couldn't figure it out.
All that time and no equipment grounds in (or outside) the home.
The first time(?) something shorts out, the breaker doesn't trip and every ground in the house is energized :-?
It was just a matter of time until someone got shocked and maybe killed.
Sorry for the long post, but it's still on my mind.
This is one time a homeowner doing his own work put his family in real danger.
Luckily (and thanks to the good Lord), nothing bad happened.
steve
ps....The appliance repairman came and found a shorted wire on the range top.
Apparently a wire (clip) had fallen loose and created a dead short to the range chassis.
"I'm getting "shocked" when I touch my A/C compressor":-?
I turn off the breaker to the unit and open the disconnect....all is well.
Turn the breaker back on and check voltage.
238V line to line, 119V line A to ground, 238V line B to ground!
What the HEY?....The ground is energized (so was the disconnect enclosure, and the A/C unit enclosure).
Good thing I was working this like it was energized (which it was).
This was on a double wide mobile home, so I start at the beginning.
Open 200A disconnect at outside pole, looks OK.
4 wire 3/0cu feeder underground to house panel....all connections tight....overhead service looks OK.
Open breaker panel inside home, and both grounded feeder conductors are landed on the (isolated) Neutral bar:-?!!.....bonding strap removed.....Equipment grounds landed on terminal strip mounted to the metal enclosure....No grounding continuity!!
The equipment grounds were not bonded to the service ground!
Actually, they weren't bonded to anything other than every grounding conductor in the home.
I start checking receptacles in the home, and some have 238V between the grounding terminal and a phase leg (Line B).
What I've got is a floating ground circuit with a short(?) somewhere that's powering up the grounding circuit.
I leave my meter on one of the receptacles with the "hot" ground and start turning off breakers.
When I get to the range breaker and turn it off, the voltage on the ground goes away.
Un-plug the range, turn on the circuit and check again, voltage gone.
I pull the range out of it's space and check for continuity at the range cord.
Sure enough, one power leg shows continuity to ground....range is shorted.
I inform homeowner that the range is defective....he needs to call repair man.
I tell him to look for shorted wire...element...etc.
To correct the house grounding, I installed a lug on the breaker panel enclosure and moved one of the grounded feeders to this lug....making continuity between the panel enclosure, circuit grounding conductors and the service ground.
When I think of this situation...and I have a lot in the last couple of days...I realize that I may have saved someones life.
It's still sinking in how dangerous this situation was for the homeowners.
I asked the homeowner who installed the electrical service to his home, and he said that he and his son did.....16 years ago:roll:.
They had tried to troubleshoot this problem but couldn't figure it out.
All that time and no equipment grounds in (or outside) the home.
The first time(?) something shorts out, the breaker doesn't trip and every ground in the house is energized :-?
It was just a matter of time until someone got shocked and maybe killed.
Sorry for the long post, but it's still on my mind.
This is one time a homeowner doing his own work put his family in real danger.
Luckily (and thanks to the good Lord), nothing bad happened.
steve
ps....The appliance repairman came and found a shorted wire on the range top.
Apparently a wire (clip) had fallen loose and created a dead short to the range chassis.