I have a place that I thought was a bad neutral. Had all the signs of a bad neutral when the HO was telling me about it.
The refrigerator motor starting smelling and making weird noises. The microwave was screeching and the smell was there also.
Dishwasher, TV, thermostat, all out in the garage with stinking motors and weird noises...
Trhe control board on the stove.... it was popping and the burning smell was there also.
All this stuff is in the garage now.
I go to the house and check the meterbase with a “super beast”. Nothing..all is good. I go through and tighten everything in the panel anyway. Nothing...
I remove the neutral from the POCO and check it also..
After all this I run a hairdryer in the house at the outlets while checking voltage. I find a circuit that goes from 123.5 to 114 when the hairdryer is turned on. I leave the dryer on and go outside to the panel. The voltage at the AFCI for that room is 123.0. Measured 12.4 amps. A 9 volt drop in a 15 amp circuit with 14/2 wire, about 25 ft of wire max. The outlets are daisy chained as usual.
The other side was 124.2.
Checked the panel with my mini Flir and read a little over 100° on the AFCI breaker that had the dryer on it for about 5-8 minutes.
This hair dryer had tripped an AFCI the week before after running for about 2-3 minutes (according to the HO)
It’s got me a little stumped.
Suggestions?
The refrigerator motor starting smelling and making weird noises. The microwave was screeching and the smell was there also.
Dishwasher, TV, thermostat, all out in the garage with stinking motors and weird noises...
Trhe control board on the stove.... it was popping and the burning smell was there also.
All this stuff is in the garage now.
I go to the house and check the meterbase with a “super beast”. Nothing..all is good. I go through and tighten everything in the panel anyway. Nothing...
I remove the neutral from the POCO and check it also..
After all this I run a hairdryer in the house at the outlets while checking voltage. I find a circuit that goes from 123.5 to 114 when the hairdryer is turned on. I leave the dryer on and go outside to the panel. The voltage at the AFCI for that room is 123.0. Measured 12.4 amps. A 9 volt drop in a 15 amp circuit with 14/2 wire, about 25 ft of wire max. The outlets are daisy chained as usual.
The other side was 124.2.
Checked the panel with my mini Flir and read a little over 100° on the AFCI breaker that had the dryer on it for about 5-8 minutes.
This hair dryer had tripped an AFCI the week before after running for about 2-3 minutes (according to the HO)
It’s got me a little stumped.
Suggestions?