Thats too simple. Are there any more transformer factors?Originally posted by kalanjeya:
1.2 factor for 277/480. @ 30Kva max load is 30*1.2= 36A
I love it. We all are still learning. At least I think we all are learning. Welcome to the club.I'am still learning.
Originally posted by kalanjeya:
1.2 factor for 277/480. @ 30Kva max load is 30*1.2= 36A
These factors seem limited to line-side Y's, since they show max current for the lowest voltages in a full boat H-N. 83A x 3= 30Kva/120Originally posted by spsnyder:
look at the secondary. I = 30,000/(1.73*208) = 83
The "factor" for the 208V equation would be 2.8
Yes, my bad. We can't keep line voltage once its phase-to-phase.Originally posted by spsnyder:
Hope that helps. We're interested in the I (line) in this question.