Anyone ever have problems with it?
I've got 53 fixtures on a circuit. All are the same and draw .23 amps at 277V. City requires that the circuit be fused at 20amps even though it's on a breaker. LCP controls 38 fixtures and wall switches and occupancy sensors control the other 15. The setup intermittently blows the 20amp fuse when the relay kicks on the 38 fixtures. When installing a 30amp fuse the system holds. I called the ballast manufacturer and they said that my inrush is 20-50X the operating current. That puts me at 175-450amps of inrush, depending on where the sine wave is when the 38 lights the are switched on.
Any thoughts on how to fix this problem?
I've got 53 fixtures on a circuit. All are the same and draw .23 amps at 277V. City requires that the circuit be fused at 20amps even though it's on a breaker. LCP controls 38 fixtures and wall switches and occupancy sensors control the other 15. The setup intermittently blows the 20amp fuse when the relay kicks on the 38 fixtures. When installing a 30amp fuse the system holds. I called the ballast manufacturer and they said that my inrush is 20-50X the operating current. That puts me at 175-450amps of inrush, depending on where the sine wave is when the 38 lights the are switched on.