Pierre C Belarge said:
There are more problems with the current/voltage relationship within buildings than in the past.
Maybe this is contributing to the 'burnout' we are seeing today.

As I said in my above post I'm quite convinced it has to do with a cheaply made product that is not made robustly enough for the environment it is in.
 

mdshunk

Senior Member
Location
Right here.
There's nothing more embarrassing to me than going back just a couple years later to replace the exact same ballast again, particularly when the room has 50 other fixtures that are just fine. I've always used Advance brand ballasts, which I have regarded as being of high quality. I really don't know what else I can do, but I do feel my reputation suffers a bit when this happens. It is hard to explain to a customer that it's out of my hands, but I did pick the ballast after all, so it is my "fault" you might say. I just hate putting so much effort into high quality work, only to be thrown under the bus by products that fail to perform.
 

iwire

Moderator
Staff member
Location
Massachusetts
I have opened a few dead electronic ballasts.

Each of the ones I opened had a blown fuse on the input wiring. Of course the fuse is soldered in place and I have no way of knowing if replacing it would fix anything or if it would just blow right away.
 

mdshunk

Senior Member
Location
Right here.
iwire said:
I have opened a few dead electronic ballasts.

Each of the ones I opened had a blown fuse on the input wiring. Of course the fuse is soldered in place and I have no way of knowing if replacing it would fix anything or if it would just blow right away.
I am left to wonder if lamps not being solidly in contact with the tombstones, or tombstones with marginal stab connections, would contribute to a sufficiently high current to blow that fuse? On another forum recently, it was advised by a knowledgeable person to check the condition of the tombstones, and the lamp connection thereto, carefully when servicing a fixture that has gone through multiple ballasts in a short period of time.
 

tyha

Senior Member
Location
central nc
have had that happen twice with the exact same problems and the first time it was a loose neutral in a j-box and the second it was a neutral was crossed and carried the load of 2 ckts on the same leg. next time you go there if all the lights are on the same circuit I will almost guarntee there is a loose neutral somewhere and if it is 2 or more circuits than the neutrals are crossed somewhere. either way it has something to do with the neutral
 

Jeff80

Member
Are you close to a power station? voltage spike when switching grids fry a ton of our electronic universal ballasts. The other thing that comes to mind is losing a neutral down line and feeding 480 to the ballasts.
 

jeffhornsby

Member
Location
Destin, FL
installing the lamps

installing the lamps

i would most likley bet it was a bad batch, but spikes, the location of a substation and installing the lamps while the power is turned can cause damage to the ballast
 