Hello all,
I have a situation where i need to wire a bandsaw. First off, motor circuits are a weak area for me since I do not do them often, so assistance is greatly appreciated. The band saw has a 2 horsepower cord and plug connected motor. So, here is what I was thinking of doing:
* Table 430.248 gives a 2HP motor an full load current of 12 amps at 240 volts
* 430.22(A) says the conductors need to be 125% full-load current, so that's 16 amps
* Table 310.16, #12 romex 60 deg C column = 25 amps
* Table 430.52 allows up to 250% for the inverse time breaker, so that's 40 amps
Now, i understand sizing breakers larger than conductors for air conditioners and the such, but how do i can around 210.21 (B)(1)? The saw has a L6-20 twistlock on it.
Should i run # 12 from a 40 amp breaker to a fused disconnect with 20 amp time delay fuses in it?
Thanks for all your input!
Jacob
I have a situation where i need to wire a bandsaw. First off, motor circuits are a weak area for me since I do not do them often, so assistance is greatly appreciated. The band saw has a 2 horsepower cord and plug connected motor. So, here is what I was thinking of doing:
* Table 430.248 gives a 2HP motor an full load current of 12 amps at 240 volts
* 430.22(A) says the conductors need to be 125% full-load current, so that's 16 amps
* Table 310.16, #12 romex 60 deg C column = 25 amps
* Table 430.52 allows up to 250% for the inverse time breaker, so that's 40 amps
Now, i understand sizing breakers larger than conductors for air conditioners and the such, but how do i can around 210.21 (B)(1)? The saw has a L6-20 twistlock on it.
Should i run # 12 from a 40 amp breaker to a fused disconnect with 20 amp time delay fuses in it?
Thanks for all your input!
Jacob