This is called an inductive choke. Needs to be bonded at both ends or changed to PVC
See 250.64(E)(1)
That whats I was looking for thank you
Sent from my iPhone using Tapatalk
It does not look like it is a grounding electrode conductor, so that section would not apply. Yes the theory is the same, but if it is not a GEC, than there is not a violation. It is very likely a non-code required bonding connection.This is called an inductive choke. Needs to be bonded at both ends or changed to PVC
See 250.64(E)(1)
How can you have an EGC run in a conduit by itself?
250.54 Auxiliary Grounding Electrodes. One or moregrounding electrodes shall be permitted to be connected to
the equipment grounding conductors specified in 250.118
and shall not be required to comply with the electrode
bonding requirements of 250.50 or 250.53(C) or the resis-
tance requirements of 250.53(A)(2) Exception, but the
earth shall not be used as an effective ground-fault current
path as specified in 250.4(A)(5) and 250.4(B)(4).
:thumbsup:This is called an inductive choke. Needs to be bonded at both ends or changed to PVC
See 250.64(E)(1)