When I've seen "bcw" on spec's, it has always meant simply "bare copper wire".Telaid said:the application is a cellular site ground system. Im reviewing a design that calls out a connection from the water main to the roof located cell building. What was specified was 2 #4/0 from the water main to the ground strap. It actually calls out 2 #4/0 awg bcw. I havent seen it before either.
The last cellulart site we did spec'ed #2 tinned copper. The BCW is most likely Bare Copper Wire, as S$ said. Copperweld would be used where strength and skin effect are paramount. Standard RG-6 also uses copperweld as the center conductor for the above reasons.Telaid said:the application is a cellular site ground system. Im reviewing a design that calls out a connection from the water main to the roof located cell building. What was specified was 2 #4/0 from the water main to the ground strap. It actually calls out 2 #4/0 awg bcw. I havent seen it before either.