4-5 Log #1680 NEC-P04 Final Action: Reject
(225.4 Exception)
____________________________________________________________
Submitter: Donald W. Zipse, Electrical Forensics, LLC
Comment on Proposal No: 4-6
Recommendation: Delete the following words from Section 225.4, Exception,
?and grounded circuit conductors?.
Substantiation: This proposal needs to be reconsidered in light of the
acceptance of Code Making Panel No. 7 to stay with their decision to make the
messenger a non-current carrying support cable.
Panel Meeting Action: Reject
Panel Statement: This exception is necessary, since it recognizes that an
uninsulated grounded conductor is permitted to be bare or covered in other
articles of the NEC. For example, Article 396 permits messenger-supported
wiring to have an uninsulated or covered messenger wire to support insulated
conductors. Another example of a wiring method permitting an uninsulated
grounded conductor is found in 338.10(B)(2) Exception covering service
entrance cable (Type SE or USE cable) where the grounded conductor is
covered within the overall jacket of the cable but would not be considered as
insulated. The grounded conductor is permitted by 250.32(B)(2) to be installed
from one building or structure to another building or structure without the
use of an equipment grounding conductor under certain considerations, with
396.10(A) permitting SE or USE cable to be used as messenger-supported
wire. Millions of miles of overhead cables with uninsulated grounded
conductors as messenger cables for service drops are installed by the utility
companies without problems.
Number Eligible to Vote: 10
Ballot Results: Affirmative: 9 Negative: 1
Explanation of Negative:
DEATON, R.: Grounded circuit conductors should be covered or insulated