Can The bare conductor in UF cable be used for the neutral for a feeder to a 240V single phase sepaerate garage panel.
The use of a bare grounded conductor is permitted in UF cable in the exception to section 338.10(B)(2)
Article 200 is Use and Identification of the Grounded Conductor, not the construction IE insulation requirements. The .1 scope of each article is a good place to start.barbeer said:200.2 gives guidelines for grounded conductors and does not infer that insulation is required. 200.6(E) is for multiconductor cables and although they mention insulated cables, my interpretation is that they are not requiring insulation.