If I have an equipment grounding conductor run with a 240v w/ a neutral circuit and there are no grounding electrodes to ground in the barn do I need to drive a ground rod?
You have to drive a ground rod, if you try to use your neutral as an equipment grounding means, then you not only risk overloading your neutral, but you will violate article 547-8(c) and article 250-32(b)(1)(2)and article 250-32(c)Originally posted by wayne123:
If I have an equipment grounding conductor run with a 240v w/ a neutral circuit and there are no grounding electrodes to ground in the barn do I need to drive a ground rod?
Please explain how using the grounded conductor as a grounding means would overload the grounded conductor?Originally posted by OneWay:
You have to drive a ground rod, if you try to use your neutral as an equipment grounding means, then you not only risk overloading your neutral, but you will violate article 547-8(c) and article 250-32(b)(1)(2)and article 250-32(c)
Originally posted by physis:
Just when I thought I understood you two guys.
Bump?
Bump, as in I bump you to the front of the line.
...For the duration of the fault, which will be very short. It is absolutely no different than a regular short circuit. Would you consider the neutral to be undersized if it were the same size as the ungrounded conductor? The ungrounded conductor is an acceptable size for a fault.Originally posted by OneWay:
When attempting to use a neutral to carry normal generated unbalanced loads AND your fault currents, you generate more heat.
It's a good suggestion, but you can't take credit for it.If you decide neither it is a good suggestion of mine to drive a ground rod at Barn and establish a grounding system there.