Using this paricular application is fine when your not trying use a neutral as a ground!%$@#get your applications right*Originally posted by georgestolz:
...For the duration of the fault, which will be very short. It is absolutely no different than a regular short circuit. Would you consider the neutral to be undersized if it were the same size as the ungrounded conductor? The ungrounded conductor is an acceptable size for a fault.Originally posted by OneWay:
When attempting to use a neutral to carry normal generated unbalanced loads AND your fault currents, you generate more heat.
Consider a service: We are allowed to have a smaller neutral than ungrounded conductors. URD is designed that way. The neutral only has to be sized large enough for the unbalanced current that could flow on it.
When dealing with a service, we're dealing with virtually unprotected conductors. It is an industry standard that the neutral of URD is smaller than the ungrounded conductors.
The reason that a 6/3 NM cable has a #10 grounding conductor is because 250.122 calls for that size EGC. Why is a #10 acceptable for carrying fault current for a 50 amp circuit fed with #6? We're talking about a tremendous amount of energy moving here, a lot of heat.
Because faulting is short-lived by nature. The NFPA took that into account when they created 250.122.
It's a good suggestion, but you can't take credit for it.If you decide neither it is a good suggestion of mine to drive a ground rod at Barn and establish a grounding system there.