Barriers for Service Panelboards
tom baker
Bremerton, Washington
Master Electrician
2017 NEC requires barriers on the incoming line terminals for service panelboards [410.3(A)(2)]. These type of panelboards have long been required in Canada, any insight on USA availability? Is it just a matter of getting the Canadian panels UL listed?
The new requirement for barriers for single disconnect panelboards in 408.3(A)(2) is inline with what UL product standard 67 requires now. This new provision provides a level of safety from contact with line side uninsulated live parts similar to the requirement for switchboards and switchgear.
I read that there will be accessory barrier kits available from manufacturers for panelboards.
Some of the 'sheilds' shown here http://www.schneider-electric.us/en/work/products/explore/service-entrance-barriers/commercial/ are not very impressive but it is a start.
The link Bob posts is to the same product that the IAEI Analysis of Changes 2017 NEC PDF slide show includes. I saw this Clip-Over-Lug-Bit-Of-Plastic for the first time just this last weekend at a continuing education class.
The implication is that UL 67 is accepting a simple snap on plastic cover that slips over each lug as meeting the requirements of 408.3(A)(2).
That's a lot less onerous than the Canadian metal enclosures over the entire line side.
These barriers appear to be for added protection while the equipment is being verified as de-energized.
They definitely are not intended to allow 'live work' inside the panel.
From the provided link:
The addition of service barriers to panelboards reduces the likelihood of electric shock but does not reduce the severity of an arc flash incident.
So if they have been required for switchgear and switchboards (which I don't install) what do those barriers look like?