Are the breakers HID listed?
I know I didn't ask and I didn't check any of the breakers for this rating. A HID rating is news to me.
A quick Google and I get the info below from 2003. This is a 240 volt service but I don't see how that matters. To me HID is HID regardless. Surely someone on the design/build end is aware of this rating? This may have an impact if we find the breakers are not HID rated. Thanks to everyone.
What do SWD and HID ratings signify? What is the difference between them?
Circuit breakers used to switch 120V or 277V fluorescent lighting circuits must be listed and marked ``SWD`` or ``HID.`` Circuit breakers used to switch high-intensity discharge lighting circuits must be listed and marked ``HID.`` UL 489 (Standard on Molded Case Circuit Breakers) permits ``HID`` breakers to be rated up to 50A, whereas an ``SWD`` breaker is rated up to 20A. The tests for ``HID`` breakers include an endurance test at 75 percent power factor, whereas ``SWD`` breakers are endurance-tested at 100 percent power factor. The contacts and the spring of an ``HID`` breaker are heavier duty, to dissipate the increased heat from greater current flow during the HID ignition period. [Courtesy of Mike Holt newsletter 10/22/03]