If anyone can help. In Nassau County is it OK to install a receptacle above electric baseboard heating ?
424.9 General. Permanently installed electric baseboard heaters
equipped with factory-installed receptacle outlets, or outlets
provided as a separate listed assembly, shall be permitted in
lieu of a receptacle outlet(s) that is required by 210.50(B).
Such receptacle outlets shall not be connected to the heater
circuits.
Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.
Same here ...that type of heat is much more even and comfortable than forced air heating. The water temperature out of the boiler (never understood why they called it a boiler) was typically less than 180°F, so the heat from the baseboard was not enough to be an issue for receptacles above it.Lived in a house with hydronic baseboard heaters once, they didn't get nearly as hot as electric baseboard heaters, also needed nearly entire length of wall because of it as well. There were receptacles above those.
Just my guess but the main predecessor to these was the old cast iron radiators and I believe they generally did have a real boiler on those systems.Same here ...that type of heat is much more even and comfortable than forced air heating. The water temperature out of the boiler (never understood why they called it a boiler) was typically less than 180°F, so the heat from the baseboard was not enough to be an issue for receptacles above it.
They did, because the system was designed to use steam, not hot water, and often had single-pipe systems where the condensed water flowed back through the same pipe as the supplied steam.Just my guess but the main predecessor to these was the old cast iron radiators and I believe they generally did have a real boiler on those systems.
Steam don't need a circulating pump either, though if return isn't or can't be designed for gravity flow condensate return pumps can be required.They did, because the system was designed to use steam, not hot water, and often had single-pipe systems where the condensed water flowed back through the same pipe as the supplied steam.
Steam is theoretically more efficient, because, like Freon, the medium changing state between liquid and gas absorbs or emits heat to a much greater degree (sorry) than mere temperature differences.