This basement area of a building is being used for lectures. It's a finished basement (nice walls, desks, etc.), but there is no carpeting. Should GFIs be installed?
metelsaatlsd said:This basement area of a building is being used for lectures. It's a finished basement (nice walls, desks, etc.), but there is no carpeting. Should GFIs be installed?
raider1 said:This sounds like a non-dwelling unit application, is it?
For non-dwelling units there is no requirement for GFCI prtoection of receptacles installed in an unfinished basement. 210.8(A)(5) is for unfinished basements of dwelling units.
Chris
stickboy1375 said:Good call Chris, got tunnel vision at the moment.