as you know an unfinished basement requires at least 1 gfci outlet . Is it okay to install this on a stud wall with nail on plastic box and nm coming down center of stud left exposed.
as you know an unfinished basement requires at least 1 gfci outlet . Is it okay to install this on a stud wall with nail on plastic box and nm coming down center of stud left exposed.
As long as 334.15 is satisfied.
As long as 334.15 is satisfied.
Just to clarify that all recep. in an unfinished basement must be GFCI protected excep. for one feeding a fire or burglar alarm.
I would say that if the NM cable follows the stud then 334.15(A) may be satisified.
Chris
If the ahj wants conduit I am screwed because I couldnt get thru the plate above I had go thru plate around corner and get the nm thru the corner stud then down to outlet 4 ft above floor. I had some mc cable but didnt want to have to set a j box to go back to n m. oh forgot I dont think mc will pass
If it's exposed, why do you have to got through the top plate?
Probably to ease the burden on the next guy when the basement is finished.
Probably to ease the burden on the next guy when the basement is finished.
Pull the pipe off, and the NM should still have the sheath on it.
Use up some sheetrock or plywood scrap and cover stud to stud the bay the wire is in. Use screws and take back down when you put finish on wall.
Use up some sheetrock or plywood scrap and cover stud to stud the bay the wire is in. Use screws and take back down when you put finish on wall.
This is what some of the Inspectors in my area require or use a GFI breaker and no need to "protect" the NM.
Im not sure if the wire protection is it , most of the time the required GFCI in an unfinished basement will be on the masonry wall and protected with emt up to above the ceiling level. Strangely enough you can finish a basement and not cover the masonry walls except with paint and the GFCI is not required.
FWIW, as far as protection against physical damage and the NEC is concerned EMT isn't one of the listed methods (unless, of course, the AHJ likes it)... no more than the flex i see ran to conceal the nm cable to furnaces and water heaters.
Pete