I suppose that if you were relying on "...in no case shall they be required to be larger than the circuit conductors..." you could be subjected to the argument that it did not say "the smallest circuit conductors", and so if you mix #12 and #14 a #14 ground would be too small.
You shoulda been an attorney. :roll: