I just have some small 120V HVAC loads, each with its own fused disc., and I just want to make sure I can wire them both to the same circuit breaker at the panel.
There are a lot of mechanical configurations of "disconnects". Some have solid neutrals, others no neutral terminal bar at all, others have the neutral going though a switch.
If the calculated load of the "small HVAC loads" does not exceed the let-through of the overcurrent protective device, and the manufacturer's instructions don't require separate circuits, then, yes.