From the NFPA 79 - Electrical Standard for Industrial Machinery
---------------------
9.1.2 Control Circuit Voltages.
9.1.2.1 AC Control Circuit Voltages.
The ac voltage for control
circuits shall not exceed 120 volts, ac single phase.
Exception No. 1: Other voltages shall be permitted, where necessary,
for the operation of electronic, precision, static, or similar devices used
in the control circuit.
Exception No. 2: Any electromechanical magnetic device having an
inrush current exceeding 20 amperes at 120 volts shall be permitted to
be energized above control voltage through contactor or relay contacts.
The contactor or relay contacts shall break both sides of the circuit
powering the magnetic device. The relay coil shall be connected to the
control circuit.
9.1.2.2 DC Control Circuit Voltages. DC control voltage shall
be 250 volts or less.
---------------
The controller this machine has uses a 230/230 transformer for the control circuit, so while it is separated from the motor currents it is still running 230Vac through the protective relays, on/off switch and emergency stop pushbuttons.
I'm just not sure where the exceptions are since I know there are a lot of machines in industry that utilize < 120Vac in their controllers. This controller is for the operation of a small <10A 3-phase motor so it doesn't meet the exceptions in the above articles.
Are there other exceptions in the NFPA 70 that I can use to accept this machine? This is quickly becoming another one of those head-scratching scenarios where I can't really think of a reason why this machine would be unacceptable except for the pretty plain black-and-white wording of this article.