Bath/bedroom remodel

Status
Not open for further replies.

flick

Member
Situation: Homeowner is converting a living room to a master bedroom. The bedroom will have a shower/toilet room in one corner. The basin will actually be installed in the open in the bedroom (not surrounded by walls).

As I see it, the GFCI for the basin will need to be on an AFCI protected circuit because it is actually in the bedroom area. The bathroom will not have a basin, and is separated with a pocket door from the bedroom area. It will not need AFCI protection. However, will I need to install a receptacle outlet in the bathroom if there is no basin?

Also, I'd like opinions on putting the lighting circuits in a bathroom on a GFCI protected circuit. Other than with shower/bath area cans that specify GFCI protection, I don't put lights on GFCI, although I often do run the lights off of the same circuit as the GFCI receptacle. This is a convenience when doing old work and is permitted in the code. Any thoughts would be appreciated.

Sorry if this has been covered before. Thanks for the replies.

John
 
Re: Bath/bedroom remodel

It's not a bathroom if no sink.So no outlet.The vanity is not a bathroom either but the gfci as well as afci are both required.gfci because its at the sink and afci because its a bedroom.Dang never thought about this but you could build a house with no bathroom :D
 
Re: Bath/bedroom remodel

Hah! I forgot the definition of a bathroom! Sometimes the obvious smacks me in the face, but usually someone else has to smack me!

Thanks Jim for reminding me of the requirements of a bathroom.
 
Re: Bath/bedroom remodel

Originally posted by jimwalker:
The vanity is not a bathroom either but the gfci as well as afci are both required.gfci because its at the sink and afci because its a bedroom.
Jim can you tell us what code section requires a GFCI near a sink in a bedroom?
 
Re: Bath/bedroom remodel

Yes, I'm going to install a receptacle at the basin, GFCI protected and on the AFCI circuit. However, I probably won't put one in the shower room unless the customer requests it. The only thing I can think of that they would want to plug in there would be a heater, and I'm installing a heater/vent/light unit anyway.

John
 
Re: Bath/bedroom remodel

I couldn't find anything in the code that requires GFCI protection for receptacles near a sink in a bedroom.

Seems to me that it should be required, though. By the same token, you could install receptacles all around the walls in the shower, but since there's no basin, it's not a bathroom, so they wouldn't require GFCI protection, either.
 
Re: Bath/bedroom remodel

Bob ,how about 210.8a7
I know it says wet bars but either we call this a bathroom sink or a wet bar.Just what would you like to call this sink ?
 
Re: Bath/bedroom remodel

NEC goofed again.They use words and give no defination.This leaves it open to a dictionary.That in turn would say its for mixing drinks.So now we have a vanity that will be used in same way as it would if it was in a bathroom with no gfci required.Perhaps we should indeed scrap the nec and start over.
 
Re: Bath/bedroom remodel

can AFI's and GFCI's be wired in series?

just wondering if there will be any nuesnce tripping?
 
Re: Bath/bedroom remodel

Many motels have the same room setup that this is.Tub/shower and a toilet in a room with a door.Just outside of it is a vanity and usually an ice bucket.If they remove the ice bucket then its not a wetbar ?
 
Re: Bath/bedroom remodel

Yes they can .Why is it that nec didn't think things out very clearly.They took the time to tell us what a bathroom was but fell short on how to handle this situation.What will the inspector want here ? I believe he will call it a wetbar.
 
Re: Bath/bedroom remodel

I started a thread a while back about doing the minimum, and this is a perfict example of what I was trying to say. The nec is the minimum. In a case like this, I would work hard to upsell the job for saftey reasons. Or I would have just put it in the bid and not looked back.
 
Re: Bath/bedroom remodel

Originally posted by jbwhite:
I started a thread a while back about doing the minimum, and this is a perfict example of what I was trying to say. The nec is the minimum. In a case like this, I would work hard to upsell the job for safety reasons. Or I would have just put it in the bid and not looked back.
Right and doing so separates you from a host of other contractors that do the minimum. :)

I still fail to see the point you are trying to make. Do you feel the NEC should require more than what is needed for safety? :)


Sorry for the rant. :roll:

Bob
 
Re: Bath/bedroom remodel

No, I dont thinkg the code should be more strict. I dont think it will ever keep up with industry changes.

I think that it is an electricians job to evaluate the situation based on experience. I believe that advising the customer is enough. Then let them decide what they want to buy.

As for the inspector issue. I agree. Like a policeman, or any other authority who enforces law, it is not his job to make the law, but to enforce it as written.
 
Re: Bath/bedroom remodel

Now what if the tub and toilet and sink was in the corner of the bedroom, no partition walls separating anything. Then the whole room would no longer need to be on an ark fault breaker. The reason I say this is because of the NEC definition of bathrooms, it has all the requirements and so therefore is not a bedroom now, but instead would be a bathroom, hence no ark fault. All the receptacles would need gfi protection, and since it has a bed it also is a sleeping quarters so per NFPA would also need a smoke detector. Seems to me like the code is actually a pretty good document, and if it was re-written from scratch, then there will always be some bozo like me to come up with ridiculous reverse ways to interpret what is mostly common sense
 
Re: Bath/bedroom remodel

when i build my dream home, i am going to have four offices and no bedrooms. I know this will make it not a dwelling unit. but i wont need arc faults.
 