Re: Bath/bedroom remodel
As Pierre and JWElectric have stated the NEC Definition of a bathroom is an AREA, not a room. The fact is that the area that contains a toilet, shower or tub, and a sink is a bathroom. A receptacle is required "adjacent" to the bathroom sink (I believe there is also something about 3'). The code requires that receptacles in "bathrooms" be GFCI protected. Since the receptacle adjacent to the sink would also be in the bedroom (whatever that is, but lets assume it is a room in which people sleep - not counting my big chair in the "living room'!) Arc Fault protection is also required. Yes, Arc Fault and GFCI can be installed on the same circuit. Since there is no sink in the room with the toilet and shower the NEC does not require that a receptacle be installed in this area, however remember that the NEC is not a design document, and that compliance with the NEC does not guarantee that an installation will be "adequate, convenient. etc.". It seems that the installation of a receptacle in this room would be a good thing, but not an NEC requirement. And yes, technically you could have a 20' X 20' room with only a tub and toilet in it and not install any other receptacles. I think that is why the AHJ is given such far-reaching authority, to make determinations that prevent contractors and home-owners from taking things to a ridiculous extreme.